6.10-stable review patch. If anyone has any objections, please let me know.
------------------
From: Rafael J. Wysocki rafael.j.wysocki@intel.com
[ Upstream commit 15cb56bd529868d9242b22812fc69bd144bfdc94 ]
If a cooling device is registered after a thermal zone it should be bound to and the trip point it should be bound to has already been crossed by the zone temperature on the way up, the cooling device's state may need to be adjusted, but the Bang-bang governor will not do that because its .manage() callback only looks at thermal instances for trip points whose thresholds are below or at the zone temperature.
Address this by updating bang_bang_manage() to look at all of the uninitialized thermal instances and setting their target states in accordance with the position of the zone temperature with respect to the threshold of the given trip point.
Fixes: 5f64b4a1ab1b ("thermal: gov_bang_bang: Add .manage() callback") Signed-off-by: Rafael J. Wysocki rafael.j.wysocki@intel.com Reviewed-by: Lukasz Luba lukasz.luba@arm.com Link: https://patch.msgid.link/6103874.lOV4Wx5bFT@rjwysocki.net Signed-off-by: Sasha Levin sashal@kernel.org --- drivers/thermal/gov_bang_bang.c | 14 ++++++-------- 1 file changed, 6 insertions(+), 8 deletions(-)
diff --git a/drivers/thermal/gov_bang_bang.c b/drivers/thermal/gov_bang_bang.c index daed67d19efb8..863e7a4272e66 100644 --- a/drivers/thermal/gov_bang_bang.c +++ b/drivers/thermal/gov_bang_bang.c @@ -92,23 +92,21 @@ static void bang_bang_manage(struct thermal_zone_device *tz)
for_each_trip_desc(tz, td) { const struct thermal_trip *trip = &td->trip; + bool turn_on;
- if (tz->temperature >= td->threshold || - trip->temperature == THERMAL_TEMP_INVALID || + if (trip->temperature == THERMAL_TEMP_INVALID || trip->type == THERMAL_TRIP_CRITICAL || trip->type == THERMAL_TRIP_HOT) continue;
/* - * If the initial cooling device state is "on", but the zone - * temperature is not above the trip point, the core will not - * call bang_bang_control() until the zone temperature reaches - * the trip point temperature which may be never. In those - * cases, set the initial state of the cooling device to 0. + * Adjust the target states for uninitialized thermal instances + * to the thermal zone temperature and the trip point threshold. */ + turn_on = tz->temperature >= td->threshold; list_for_each_entry(instance, &tz->thermal_instances, tz_node) { if (!instance->initialized && instance->trip == trip) - bang_bang_set_instance_target(instance, 0); + bang_bang_set_instance_target(instance, turn_on); } }